240V AC questions ...
Re: 240V AC questions ...
and now you can also go fishing and cook fish for wife who is very happy you are not dead. win, win 
0 x
-
Bootstrap
Re: 240V AC questions ...
That's funny!violet wrote:and now you can also go fishing and cook fish for wife who is very happy you are not dead. win, win
I do find my life goes better when I don't do things that make my wife nervous. Which is why I did not buy that motorcycle...
FWIW, the new cooktop works MUCH better than the old one. Looks nicer, too.
0 x
-
Wade
Re: 240V AC questions ...
Moral of the story: Us men can think things through, have all kinds of good ideas that may even be more logical then our wife's, but in the end her ideas will probably just work out better anyway... 
0 x
-
Judas Maccabeus
Re: 240V AC questions ...
Induction cooktop?Bootstrap wrote:That's funny!violet wrote:and now you can also go fishing and cook fish for wife who is very happy you are not dead. win, win
I do find my life goes better when I don't do things that make my wife nervous. Which is why I did not buy that motorcycle...
FWIW, the new cooktop works MUCH better than the old one. Looks nicer, too.
J.M.
0 x
-
Bootstrap
Re: 240V AC questions ...
No, I have inherited cast iron skillets and pots from my family and I love to cook with them, I just don't want to buy a bunch of new-fangled pots and such.Judas Maccabeus wrote:Induction cooktop?
It's this model:
GE JP5030DJBB - 30 in. Radiant Electric Cooktop in Black with 4 Elements including Power Boil Element
0 x
-
Judas Maccabeus
Re: 240V AC questions ...
Nice. Wish i had that kind of flexibility.Bootstrap wrote:No, I have inherited cast iron skillets and pots from my family and I love to cook with them, I just don't want to buy a bunch of new-fangled pots and such.Judas Maccabeus wrote:Induction cooktop?
It's this model:
GE JP5030DJBB - 30 in. Radiant Electric Cooktop in Black with 4 Elements including Power Boil Element
J.M.
0 x
-
ohio jones
Re: 240V AC questions ...
Whoa there, Waylon. Now that we know the model number and can look at the manual for ourselves, we see that you can indeed use a 30A breaker on a 208V circuit which would come from a 120/208V three phase panel. For a 240V circuit, which is what you have on a typical 120/240V single phase residential service, the maximum current draw is 30.4A, which would overload a 30A breaker.Bootstrap wrote:Electrician shows up. Waylon, about 30 years old, smells like cigarettes, huge smile, engaging, strong twang, smart guy. Knows a LOT about fishing and how to catch various kinds of catfish and where to find them locally, happy to tell you all about it as he works. Looks at the circuit box. Walks over to the stove box, pulls out the manual, reads it slowly. Looks up at me and says, you know, you can also run this on a 30 amp circuit ...
In practical terms, it's perfectly safe if you never use all four elements at the same time. But just in case you forget that on Thanksgiving morning, and in consideration of future owners if you sell the house, upgrading the circuit would be the right thing to do.
0 x
-
Judas Maccabeus
Re: 240V AC questions ...
You think they are that precise? Most modern breakers are of the delay trip type. Will take a load in excess of 30 for a brief period.ohio jones wrote:Whoa there, Waylon. Now that we know the model number and can look at the manual for ourselves, we see that you can indeed use a 30A breaker on a 208V circuit which would come from a 120/208V three phase panel. For a 240V circuit, which is what you have on a typical 120/240V single phase residential service, the maximum current draw is 30.4A, which would overload a 30A breaker.Bootstrap wrote:Electrician shows up. Waylon, about 30 years old, smells like cigarettes, huge smile, engaging, strong twang, smart guy. Knows a LOT about fishing and how to catch various kinds of catfish and where to find them locally, happy to tell you all about it as he works. Looks at the circuit box. Walks over to the stove box, pulls out the manual, reads it slowly. Looks up at me and says, you know, you can also run this on a 30 amp circuit ...
In practical terms, it's perfectly safe if you never use all four elements at the same time. But just in case you forget that on Thanksgiving morning, and in consideration of future owners if you sell the house, upgrading the circuit would be the right thing to do.
Of course the electrician likely knows that
0 x
-
Bootstrap
Re: 240V AC questions ...
OK, now I'm back to not knowing.
If I need a 40 amp circuit, at least I can have the satisfaction of believing I read the manual correctly the first time. If I can get away with a 30 amp circuit, I can have the satisfaction of thinking my money was well spent and being happy with Waylon.
Which form of satisfaction should I want? Is OJ right or is JM right?
If I need a 40 amp circuit, at least I can have the satisfaction of believing I read the manual correctly the first time. If I can get away with a 30 amp circuit, I can have the satisfaction of thinking my money was well spent and being happy with Waylon.
Which form of satisfaction should I want? Is OJ right or is JM right?
0 x
-
AnthonyMartin
- Posts: 1240
- Joined: Thu Jun 13, 2019 8:52 pm
- Affiliation: LMC
Re: 240V AC questions ...
Most cook tops are fine with 30 amp. The only danger would be if you didn't have heavy enough wire on a higher level circuit. For instance, if you put a 40amp breaker in without upgrading the wiring. The worst that could happen with a 30amp for you now is that the breaker might flip leaving your food uncooked.Bootstrap wrote:OK, now I'm back to not knowing.
If I need a 40 amp circuit, at least I can have the satisfaction of believing I read the manual correctly the first time. If I can get away with a 30 amp circuit, I can have the satisfaction of thinking my money was well spent and being happy with Waylon.
Which form of satisfaction should I want? Is OJ right or is JM right?
0 x